kallileo
Lifetime Supporting Member
I have panel which controls a batch pasteurizer. The panel has an E-Stop and a safety relay (Schneider XPSAC5121) which cuts power from all DOs of the PLC and the STO contacts of and ac drive which drives an agitation motor.
Now there a special application where I also need to add a Fail-safe inductive sensor (IFM GI505S) to monitor the lid and stop the agitator (STO) when it's opened during operation so I have to add second safety relay (IFM G1501S) just for the prox sensor.
I was thinking about how to wire the safety relays properly.
First option is to wire the safety contacts of both safety relays and the STO signal in series. This way when the E-Stop is pressed or the lid is open the agitation stops.
Second option is to use the safety contact of the E-Stop safety relay to cut the power to lid monitoring safety relay (IFM). So when E-stop is pressed everything stops but when the lid is open on the agitation process stops.
What do you think?