Hi guys,
We've a customer plant running about 10 sets of PLC 5 redundant, some of them has a few IO rack due to large quantity of IOs in the system. All PLC 5 are linked using DH+. These 10 machines are running independant. With the new budget approval they'd like to upgrade the PLC 5 CPU (mostly PLC5 40 and 60) to ControlLogix. While the IO will be still using PLC 5. We've not done any upgrade from PLC5 - CLX before.
Appreciate if anyone has done this can give me some advise what shall we check & clarify on the PLC 5 redundant system and shall we take good care?
We are thinking to propose to use redundant CLX running ControlNet + add an additional ControlNet module at the PLC-5 IO rack.
The PLC-5 ladder program should be rewrite manually in CLX style, right?
Thank you.
We've a customer plant running about 10 sets of PLC 5 redundant, some of them has a few IO rack due to large quantity of IOs in the system. All PLC 5 are linked using DH+. These 10 machines are running independant. With the new budget approval they'd like to upgrade the PLC 5 CPU (mostly PLC5 40 and 60) to ControlLogix. While the IO will be still using PLC 5. We've not done any upgrade from PLC5 - CLX before.