Aabeck Member Join Date Feb 2013 Location Detroit Posts 1,860 Nov 21, 2019 #16 alive15 said: Yes, I agree about the grounds. What about the commons / neutrals for 24VDC? Click to expand... Unless the power is shared through the different units/panels then I would not run commons between them if not needed.
alive15 said: Yes, I agree about the grounds. What about the commons / neutrals for 24VDC? Click to expand... Unless the power is shared through the different units/panels then I would not run commons between them if not needed.
alive15 Member A Join Date Oct 2015 Location Montgomery, AL Posts 721 Nov 22, 2019 #17 Aabeck said: Unless the power is shared through the different units/panels then I would not run commons between them if not needed. Click to expand... What are the consequences of doing such things? I don't want to experiment, haha, but maybe someone else has more experience than me ))
Aabeck said: Unless the power is shared through the different units/panels then I would not run commons between them if not needed. Click to expand... What are the consequences of doing such things? I don't want to experiment, haha, but maybe someone else has more experience than me ))
Aabeck Member Join Date Feb 2013 Location Detroit Posts 1,860 Nov 22, 2019 #18 Potential short circuits shutting down the 24V power supplies or blowing fuses. And, ina panel that the problem might not be in.
Potential short circuits shutting down the 24V power supplies or blowing fuses. And, ina panel that the problem might not be in.
jholm90 Member J Join Date Mar 2012 Location Ontario Posts 155 Nov 22, 2019 #19 Better put the old lever limit switch back in.. nice and durable without that extra common wire nonsense
Better put the old lever limit switch back in.. nice and durable without that extra common wire nonsense
daba Lifetime Supporting Member D Join Date Jul 2004 Location uk Posts 5,401 Nov 23, 2019 #20 Why not just get a 2-wire proximity sensor ? They only cost a few dollars. You can always drive an optical isolation relay in the panel with it if it is not compatible with your inputs.
Why not just get a 2-wire proximity sensor ? They only cost a few dollars. You can always drive an optical isolation relay in the panel with it if it is not compatible with your inputs.