I have a 24v prox with three wires. I do not have COM available for 24v+. Can I just use the 24v+ & GND to power the sensor? It's not a critical input. It just sees a part. If the sensor fails, nothing will move after that.
 
When you say 24V+ and GND, do you mean 24V+ and (what we down under would call) earth? i.e. provide 24VDC and tie the 0V wire to the metal frame of [something]?

If I have the above correct, it will work if the DC power supply has the negative connected to earth (ground) also. If not, no.

As to whether you should...no. No, you should not. I've seen it done plenty of times in a pinch, to get a machine running at 3am, but it's not a good idea. You're forcing the metalwork and the earth conductors to be a part of your current path, and that's just not the right thing to do, unless you're doing auto electrics.

Run a new cable.
 
If you have 3 wires that is typically all you need. 24vdc. Common. And signal return to the input. That is 3 wires. Then run a jumper from either 24vdc or common depending on your input type (sourcing or sinking)

Edit

Don't use ground as a 4th wire as it's meant for safety and not for carrying current. If the input is of different voltage the. You can use a 24vdc relayat the other end.
 
Last edited:
Don't do it it's a very bad idea
While you may get it work for a while but if the ground loop changes you could end up with all kinds of problems intermittent operation
Also you could never get it inspected if they see it ground conductors may never carry any current
the Ground or Earth is there to make sure that all metal parts are at the same earth potential
If you cant run a simple 3 conductor cable to the Prox then maybe you should not be using it.
 
If I understand correctly, you are asking if you can use an earth ground instead of a 0VDC common terminal point.

If your 0VDC is bonded to your earth ground, I suppose you could. Having the neutral tied to earth ground in AC is pretty standard, but I have found having 0VDC tied to earth is not as automatic. Double check - It may not be connected/bonded to earth ground.

That said, even if it is, you will probably run into ground loop issues. Don't rely on the earth bonding to complete your sensor's circuit.
 
Question on grounds and commons, is it acceptable to tie the grounds between two different panels that have two different power supplies (AC or DC)? What about tying 24V common / neutral between two different power supplies?

From my understanding, it is okay to tie the grounds together. However, for the 24V common, the current will take path of least resistance, so most likely it will stay within the circuit of it's own panel anyways. I guess my question is, is there any benefit to tying the commons together, if it's allowed in the first place?
 
sorry I misread the post, I now understand that it was a 3 wire (well by the sounds of it a 3 wire + earth) with one broken off why not just say that. a statement like "I have a 24v prox with three wires. I do not have COM available for 24v+." is a poor English explanation in my book.
In that case Using the earth (if it is one) probably would not work unless it is internally connected to the -ve (com). For the cost of a sensor why not just buy one.
 
Question on grounds and commons, is it acceptable to tie the grounds between two different panels that have two different power supplies (AC or DC)? What about tying 24V common / neutral between two different power supplies?

For grounds it is usually a good idea to ground everything connected together into one common bonded ground point. There can be a potential voltage between 2 separate ground rods on panels at different locations, and if the panel and the machine have individual ground rods.

Always try for a single ground point and have good bonding throughout.
 
For grounds it is usually a good idea to ground everything connected together into one common bonded ground point. There can be a potential voltage between 2 separate ground rods on panels at different locations, and if the panel and the machine have individual ground rods.

Always try for a single ground point and have good bonding throughout.

Yes, I agree about the grounds. What about the commons / neutrals for 24VDC?
 

Similar Topics

I have a project to automate four generator sets. The system will monitor and store the load demand of the factory. Once there's Power outage, the...
Replies
0
Views
64
Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
Replies
3
Views
124
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
222
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
60
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
113
Back
Top Bottom