I have a problem comming up with the best solution for after switching from manual mode to auto to balance valve posistion.

1. Valves have posistion resistors monitored with converters, 0-10v into PLC

2. Manual mode two valves opened and closed thru switches on
panel.

3. When returning to Auto mode combined % open added together for a % value needs to be balanced between the two valves.

example-

% open among both valves added together is 40%

valve 1 = 25%
valve 2 = 15%

need both to balance at 20% each maintaining the 40% total.

Using RSLOGIX 5000
 
I take it that the valves are set via open/close pulses
Add the 2 feedback signals, divide by 2 and use that value to set the output for bump-less transfer. When you go to Auto one valve will open to 20% the other will close to 20%.
I may have miss-interpreted your question.
Just because the signals still add to 40%doesn't mean the flow will be the same as before. The flow to valve position is not a linear relationship.
Tell us a little more about yor process.
Regards
Roy
 
My 2 cents,
After the switch goes from Man to Aut just force the 2 analog outputs to 2V (20%)for a certain time, before you go to full Auto mode.
 
Nonuke,
The poster said the valves are driven by switches, I assume one for Open one for Close, your idea is good though. Perhaps compare the voltage feedback to 20% (Total/2) and drive valve until the two match.
I can't help thinking it's a bit strange what he is doing. If you set the valves up in Manual why would you want to upset everything when you switch back to Auto. It's normal to start where you were (Bumpless Transfer)
Roy
 
Thank you for your replys much help! When in auto I don't control the valves independently. so i would like them to be as close as possible to each other.
 

Similar Topics

Good morning, We've had an issue with a couple of servo valves and was wondering if anyone had seen anything similar. After a drop in pressure...
Replies
2
Views
119
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
Replies
4
Views
191
I have been requested to test this proportioning valve for PLC control of flow/pressure. Dwyer Series SVP Proportioning Solenoid Valve The flow...
Replies
10
Views
433
Hi Everyone, Thought I had it figured out but I came to the conclusion it would not work. Here is what I'm working with... 1769-L30ER Flow Meter...
Replies
24
Views
729
So I'm pretty green when it comes to troubleshooting in the field so bear with me. We have a Danfoss valve that opens/closes from an analog output...
Replies
23
Views
983
Back
Top Bottom