So I'm pretty green when it comes to troubleshooting in the field so bear with me. We have a Danfoss valve that opens/closes from an analog output card in a remote PLC rack. I can see that we are trying to send full open (20mA) from the program but the valve will not move. Could someone explain step-by-step the process to check amperage from the card to see if it is actually sending 20mA? I'm trying to not blow anything up if I can help it. And yes, I have a process meter that can simulate amps. Also, I know it's not a bad Danfoss valve because it is only showing 1.845 mA via interface of the valve.
I'll try to elaborate a bit more on what Mas01 tried to say, as it wasn't very clear for someone who may not have ever done any testing.
There are multiple ways you can check a 4-20 signal output and verify it's at least coming out and/or scaling right for the called output.
If you don't know exactly what % output it's supposed to be, you'll be in trouble. but otherwise you can still do these and see changes and verify you have output.
There will be a couple of wires for your analog output. you only need to deal with the 1 signal wire if you are using a meter in series to check.
1) disconnect the signal wire from the Analog out. usually the return line is labeled 'Ret' or 'Return', you can leave it on.
2) take the leads of your meter and put them in the mA and Com positions. then set the meter to mA reading.
3) connect 1 lead to the wire you disconnected, and the other wire to the terminal you took the wire off of. the meter should be in series with the connection that was there before. if you connect in parallel you'll just blow your meter fuse.
The second way to test an output is to take the signal and return wires off. and install a 500 ohm resistor on the signal and return lines.
now use a meter and test DC Volts. this converts the signal from 4-20mA to 0-10 Vdc. so 4mA = 0v, 8 mA = 2.5v, 12mA = 5v, etc etc.