VFD install on open delta system
Just as an FYI, I have received confirmation from the power company that they have 4-wire high-leg open delta, but they are hoping/planning to move away from it.
Yes. Look for what's often referred to as a "Drive isolation transformer". It will be a 240V delta primary, with a 240?137V wye secondary. You will ground the center point of the wye, but you need not run that as a neutral, because 137V is useless for anything, it's just there to keep the power electronics referenced to a consistent ground point.
I have a VFD rated for 125HP at 480V. After the VFD, there is a sine wave filter, then a 480/240 150KVA transformer, before the 100HP motor...
3,211
Little PF525 was wired in and set up to run on power up. Disconnect for this is over 200 feet away. See the reversing starter? Yep, that is how...
1,661
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
69
Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
123
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...