Hi guys. I´m new here in this site although I´ve been working in automation for some time.
I received a project where I need to monitor either the frequency or the voltage value from a generator and make sure they stay within limits. Both frequency and voltage go up or down together according to the load attached to the generator, so I only need to monitor one of them.
This sounds really simple although I couldn´t find anyone selling a sensor I can use to sense voltage or frequency and input that value into the PLC.
I bet somebody else run into something like this.
Do I need a custom electronic module to convert from either frequency or voltage for the analog PLC input?
Thanks a lot.
Thanks a lot.
Personally i would use a power meter with communications such as Modbus etc. and read that back to the PLC:
http://global.powerlogic.com/products/meters_and_rtu/
Just a thought but couldnt you monitir a tach pulse or an encoder on the motor?Im sure motor RPM would relate to both qtys you are trying to monitor.
Hello,
you can use a powermeter from Merlin Gerin Type PM500 (old model) or the model PM700 (newest is yet PM800) in combination with module 1AO.
This gives a analogue output 4..20 mA that you can read in the PLC. Within the PM700 you can set the range to this channel 0.400VAC or 0..50 Hz of KVA or KWh or ... (whatever you want). Then in the PLC you can scale it also and make some alarms of it.
Greetz (sorry for my englisch, its not so best)
You might consider a Frequency Input Signal Conditioner such as the Dataforth DSCA45 frequency input module which provides a single channel of frequency input which is converted to a standard analog voltage or current output.
I normally use a Crompton blind digital power monitor and pull the info out via Modbus RTU.
Alternatively put an extra mag pick up on the fly wheel and use a high speed counter to monitor speed. Just be carefull though as mag pick ups work at fairly low voltage levels. Woodward have them for sale.
hi
if u are using an AB PLC you can go for AB make power monitor and get data by messaging or u can take any energy meter which supports modbus communication
I have a Powerflex 70 that recently fried in a power outage. The drive is connected to two permanent magnet AC motors via two contactor/overload...
2,493
tonight i was called on an inverter that kept faulting on overcurrent (F18,,TBwoods Etrac inverter 4001),,what was happening was after the...
29
10,903
Hello all- I have a unique challenge using a customers Direct logic 06 PLC. This customer has a DC motor operating at 10 RPM which is turning a...
142
I've got 6 identical regenerative vacuum blowers powered by 6 identical drives in 3 identical panels all fed from the same 1 main building feed...
27
890
Hi all, We are currently experiencing an DC over voltage fault on one of our inverters. During commissioning a snag was raised whereby excess...
204