Thats right. I have a few PLCs that are in foreign plants where there is no one on the maintenance staff that has enough PLC experience to trust that they would be able to solve PLC problems. So I put in some extensive diagnostic screens in RSView - and one screen allows them to view the processor status, clear a fault code, and place the PLC back into remote run (provided the key is in REM), as well as set the processor time. It is simply a matter of creating the RSView tags to read/write from/to the status file bits. I also added the RSLadder (ladder viewer) Active X to a diagnostic screen so that they can view the running ladder from withing RSView, and with a small bit of VB programming there is a password protected button that allows a re-download of the program to the PLC. I don't normally put those features into an RSView app, but in this case it has saved me at least one trip across the pond.