when do you select TTL Sourcin/ Sinking Input/Outputs card

bioplc

Member
Join Date
Jul 2005
Location
tampa
Posts
97
Can someone kindly explain, when do i select a TTL Sourcing or Sinking Input/ Output module over other module.

Thanks in advance.
 
I pick my cards based on what external hardware I have. IE...is the sensor PNP or NPN.

IF the sensor is a NPN then I will need sourcing cards
If the sensor is PNP then I will need sinking cards.

Output Card are decided the same way (well I decide the issue the same way) Does my device require a sinking our sourcing signal.Have worked with VFD drives that required a sinking signal from the PLC to operate.

If worst comes to worst and you pick the wrong card you can install interposing relays are use a pull up resistor (personally I would change the device or the card)
 
TTL as I understand it means transistor to transistor logic.

I have heard people refer to a ttl card when needing a card that operated in the 5 vdc range. I know that AB lists there 5VDC cards as TTL cards.

Hope that helps
 
As far as I know, TTL output is always sinking.
Why use TTL input/outputs? To work with TTL level signals which are incompatible with typical PLC DC inputs.
For instance, now discontinued Omron barcode reader sensor V500something had Match/No Match TTL outputs.
 
Last edited:
Some clarification: actually, TTL is a voltage output with sinking active level of signal.
Not to be mixed with sinking open collector, line driver and tri-state 5V rated outputs.
 

Similar Topics

Im trying to install a Siemens upgrade license using Automation License Manager v6.0. I clicked D: mistakedly, and now I can not find a way to...
Replies
2
Views
64
Hello, We recently upgraded our control server to a newer model. After the transition we are experiencing issues with our trend graphs to where...
Replies
2
Views
130
Hi all, I really need help with this one. I'm at a complete loss... For months and months, I've had no problems with pressing a NEXT button to...
Replies
14
Views
1,458
Hello everyone, I'm having trouble solving this one and was hoping someone could help. I have a AB CompactLogix L16ER PLC connected to a AB...
Replies
2
Views
594
Is there a way to select a parameter file when loading a given screen based on the value of a variable? I see that under "Global Connections" the...
Replies
2
Views
1,123
Back
Top Bottom