You could open it now...I hope...I set neutral language...Good night
there are several errors when i try to compile it
1. Description of Error:
The called block is not available, it must be compiled before being called.
To Correct or Avoid Error:
In the case of system function block (SFB)/system function (SFC) calls, copy to your offline database using the SIMATIC Manager. If the called SFB/SFC is not available on the addressed CPU, it must not be called.
2. Description of Error:
Only one instance DB can be automatically generated for each S7-GRAPH FB. During an automated process for generating a DB, the system found an S7-GRAPH FB that contains two instance DBs in the project.
To Correct or Avoid Error:
Open the S7-GRAPH FB and generate the two instance DBs manually and in sequence.
3. Description of Error:
This is just a warning. No type description is available for the block you called.
To Correct or Avoid Error:
Check the language settings in the Program Editor which also determine the offline database.
4. Description of Error:
Syntax errors are present in the compiled file or in the user entry. If a "Details" button is displayed, click it to find out more about the cause of error.
To Correct or Avoid Error:
Check your entries.
Maybe a more experienced person can help you with it, tried to but i think here it stops for me sorry men