Wind-Unwind Troubleshooting (with graphic)
AutomationTechBrian
Jul 2013
St. Cloud, MN
669
I was working at a customer's location yesterday and I came across an intermittent issue on their wind/unwind machine. I'm still trying to figure out what is causing it, but I thought I'd share a graphic for those who have a little experience with this application.
Hardware:
3, ABB ACS 800 drives with wind/unwind firmware... 2 unwind, 1 wind-up
1 Siemens HMI, with PLC program software (step 7)
Profibus Network, HMI to the 3 drives.
Fiber optic connection between the 3 drives.
Load cells, for tension control. Feedback to the 2 unwind drives.
Simple control system:
HMI is used for entering values, including tension set point and roll diameters.
Profibus feeds the values into the drives.
Application is run by the drives.
There is an intermittent issue, that is illustrated by the graph. The second line is the load cell feedback for the paper unwind roll. The other 3 lines are the torque feedback from the drives... 1. Paper, 3. Windup, 4. Poly
I did several studies on the signals using an analog data logger. This particular one captured the intermittent anomaly perfectly. You can see near the beginning, the torque for BOTH the paper and the windup roll increase at the same time the load cell drops. The situation remains unstable for a section of time, then it comes back into control about 3/4 the way through the cycle. You can see a decrease in torque in both rolls at the same time, then "normal" until the end.
I'm suspecting the feedback signal from the load cell is to blame, since the situation doesn't seem to affect the poly torque. I just don't know how to isolate the different aspects of the load cell signal yet to confirm my theory. I wish I could have a second device to confirm whether the tension really drops when the load cell signal drops.
Any thoughts would be appreciated. The customer wants us to update this machine, since the components are soon to be obsolete. I'm working on the learning curve right now as time allows.
Just FYI...
We isolated the problem today. It was the signal from the load cell, before it reached the amplifier.
Got some good experience troubleshooting load cells with intermittent issues.
Hi all. First time programming a machine of this type. A center driven unwind feeding to a center driven rewind. No dancers or load cells, just...
37
4,904
I'm doing my first wind/unwind project, and I need some input from someone with more experience. ...I'm getting my butt kicked trying to control...
38
11,349
Hi All, I am currently programming a rotational cycling machine that is meant to rotate parts one direction a predefined number of degrees and...
3,324
Good Morning. I will be designing a unwind station to provide material to a nip roll that runs at a constant speed once dialed in by the operator...
2,875
Hi all, I am a new hand of AB servo. When I read the manual, there is a term that I don't understand. Could anyone explain it to me, what does...
2,878