Wiring Flex IO 1794 ie12 analog input module with BT 1794 TB3G
joaco1993
Sep 2014
newyork
237
Could someone show me an example on how to wire the analogic input for lets say channel 0 ??
Ive found this manual http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1794-um062_-en-p.pdf
I would do it as in the picture i attached.. but dont know if its correct.
Another question, i will simulate the input. I will introduce the simulator in the circuit where it says SENSOR, but when I meassure Voltage between the two terminals of the simulator I see 31Vdc, will there be a problem as I also have the 24Vdc powersource in serie ??
I tested it and seemed like it worked okay, but cant understandy why. Before I put the simulator, i unpluged the sensor, and meassure Voltage between + and - terimnals where the sensor would be conected and saw 24Vdc, after I plugged the simulator and when I meassured the two terminals of the simulator i saw 24vdc, but before i was seeing 31vdc. Im missing something and dont get it.
Another question, if screw B-17 isnt connected to the common, is left unwired, would the input work ?? i mean B-17 is internally connected to the common C-35 ??
Hi all, what is the proper way to fuse 1794-IE12 modules? fuse sizes/locations? We are burning up these modules in our facility.
1,734
Hi guys, I am new to Rockwell Platform and do not understand How to do the wiring of IB32 module. and at terminals 35-51, is Voltage available on...
3,098
I have a powerflex 525 that runs on 220 VAC. I wired up power and got into some parameters, but for the most part left it alone. I then got a...
1,979
So i’m Field engineering a panel for a 19’ conveyor we are building. The conveyor will have 3 - powerflex 4 drives. My question is concerning the...
2,435
Issue is I have been provided with a A-B typical for an SMC-Flex, with no parameters beyond the fact that it states that I need to change the...
3,855