OK, you are still not giving us enough to give you a good answer but it seems you want to install a VSD with an RFI filter protected by an E-Stop circuit. Are you controlling it from a PLC, a pushbutton? What is the machine or system? Is there a guard circuit? A more complete description than a single line is required.
The basic function you seem to want is to cut power to one or more contactor/s upstream of the VSD, and prevent restart until the relay can see that all contactors have opened. This is relatively simple to design and wire. Look up some of the links I posted earlier for some example schematics of practical circuits. Pilz provide a great deal of example drawings in their catalogue for using an E-Stop relay to protect a motor. I strongly suggest downloading this and reading it carefully until you understand how this works.
Regarding EMI protection on VSDs, do a search on this site for this. You may find that simply using shielded cables is sufficent, but since you have said nothing about your installation I am not going to guess.
Note: if you don't have an electrical trades or engineering qualification you should be very wary of designing a safety circuit, since if it fails then you will be personally exposed to lawsuits. Pay an engineer or electrician to design and install the circuit for you.