I want to be able to use a 3rd party device to read the IO modules from an SLC505 without the use of the CPU. All the communications modules i come across appear to require the use of the CPU to pass thru the data.
MODULE Slot4 (Parent := "SLC_Adapter",
ParentModPortId := 1,
CatalogNumber := "1746-OW16",
Vendor := 1,
ProductType := 116,
ProductCode := 41,
Major := 1,
Minor := 1,
PortLabel := "RxBACKPLANE",
Slot := 4,
Mode := 2#0000_0000_0000_0000,
CompatibleModule := 1,
KeyMask := 2#0000_0000_0001_1111,
SafetyEnabled := 0)
ExtendedProp := [[[___<public><PL>02<Version Name=$Q2.13$Q/></PL><CatNum>1746-OW16</CatNum></public>___]]]
ConfigData := [8,4,4,0];
ConfigScript (Size := 84) := [78,0,0,0,4,0,0,0,0,0,0,0,0,0,0,0,62,0,0,0,7,1,0,0,0,3,0,0,0,12,0,0,0,1,0,29,0,0,0,2,0,0,0,0,0,3,2,0,0,0,0,0,0,0,32,0,0,0,2,0,0,0,2,0,0,0,34,0,0,0,16,0,0,0
,16,0,0,0,64,0,0,0,0,0];
CONNECTION _21000B0324042C112C12 (Rate := 20000,
InputSize := 4,
OutputSize := 2,
EventID := 0,
Priority := Scheduled,
InputConnectionType := Unicast,
InputProductionTrigger := Cyclic,
ConnectionPath := "21 00 0b 03 24 04 2c 11 2c 12",
InputTagSuffix := "I",
OutputTagSuffix := "O")
InputData := [0];
OutputData := [0];
END_CONNECTION
I think you are over estimating my ability Ken. But I keep learning by reading your posts in PLCTalk. I appreciate very much your input. For example, it did not occur to me the other day exporting the LK5 file, and I was trying to decode the forward open request after getting a Wireshark trace.Alfredo is probably the PLCTalk forum member with the most direct experience using CoDeSys with 1734 POINT.
I think I'm in agreement with your decoding! I'm leaving for the weekend so I'll get back to it Monday and hopefully our module arrives so I can quit probing this CPU and get to the fun stuff!!
Thanks again.
21 00 0b 03 Class 0x030b = 779 decimal
24 04 Instance 0x04 = 4 decimal
2c 11 Attribute 11 (input ?) = 17 decimal
2c 12 Attribute 12 (output ?) = 18 decimal