AB PLC5 BTW/BTR Block

Dear Pros,

Need help on converting PLC5 to Studio 5000.
I found few BTW/BTR block pointing back to Rack 000, group 0, module 0, which should be the CPU module. The weird part is the length is 0. Is length 0 mean the BTW/BTR block not in use anymore?

Or this is actually some technique to get some hardware status?
Attached some print screen for the logic.
Attached Images
File Type: png Print Screen 1.PNG (102.9 KB, 16 views)
File Type: png Print Screen 2.PNG (102.4 KB, 12 views)
  Reply With Quote
Old July 28th, 2021, 06:18 AM   #2
drbitboy
Lifetime Supporting Member
United States

drbitboy is online now
 
drbitboy's Avatar
 
Join Date: Dec 2019
Location: Rochester, NY
Posts: 3,336
https://literature.rockwellautomatio...C728%2Cnull%5D
yyy.png
__________________
i) Take care of the bits, and the bytes will take care of themselves.
ii) There is no software problem that cannot be solved with another layer of indirection.
  Reply With Quote
Old July 28th, 2021, 08:50 AM   #3
Operaghost
Member
United States

Operaghost is online now
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 3,323
The CPU in a PLC-5 system does not have a rack address. Rack 0, Group 0 Module 0 would be the first slot to the right of the CPU. The length of 0 means whatever that module has available (read) or will accept (write). It was a default setting for when you didn't want to have to look up the actual number of words to read or write. When managing memory, it meant that you had to assume it would use 64 words. You wouldn't just say 64 (the maximum) because if the module had less than that it would cause an instruction error. So using 0 was very common.

OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar

Last edited by Operaghost; July 28th, 2021 at 08:54 AM.
  Reply With Quote
Old July 28th, 2021, 02:48 PM   #4
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 1,657
It looks like they wrote the block transfer and then never actually finished
Length of 0
I believe the rack 0 and group 0 I. The processor
In logix5000 you need need to use messaging
  Reply With Quote
Old July 28th, 2021, 03:42 PM   #5
Operaghost
Member
United States

Operaghost is online now
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 3,323
Quote:
Originally Posted by Operaghost View Post
The CPU in a PLC-5 system does not have a rack address. Rack 0, Group 0 Module 0 would be the first slot to the right of the CPU. The length of 0 means whatever that module has available (read) or will accept (write). It was a default setting for when you didn't want to have to look up the actual number of words to read or write. When managing memory, it meant that you had to assume it would use 64 words. You wouldn't just say 64 (the maximum) because if the module had less than that it would cause an instruction error. So using a length of 0 was very common.

OG
I've never had to quote myself before. Emphasis added.

OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
  Reply With Quote
Old July 28th, 2021, 08:40 PM   #6
koyeap
Member
Malaysia

koyeap is offline
 
Join Date: Feb 2013
Location: Selangor
Posts: 17
oh I see, thanks a lot! sorry i missed out the 0 is reserve for maximum in manual.

Next module to CPU is a backup comm module(BCM), which mean this block transfer is for redundancy data exchange purpose? or is connect to 3rd parties devices?
  Reply With Quote
Old July 28th, 2021, 10:24 PM   #7
koyeap
Member
Malaysia

koyeap is offline
 
Join Date: Feb 2013
Location: Selangor
Posts: 17
Quote:
Originally Posted by koyeap View Post
oh I see, thanks a lot! sorry i missed out the 0 is reserve for maximum in manual.

Next module to CPU is a backup comm module(BCM), which mean this block transfer is for redundancy data exchange purpose? or is connect to 3rd parties devices?
Since I am going to upgrade the PLC5 to 1756 Series, which mean if this is for redundancy purpose then i can ignore the BTW/BTR in new logic right?

Thanks
  Reply With Quote
Old July 29th, 2021, 09:21 AM   #8
Operaghost
Member
United States

Operaghost is online now
 
Operaghost's Avatar
 
Join Date: Apr 2002
Location: Dallas, TX USA
Posts: 3,323
The BTR/BTW for the BCM modules was a method to transfer data from one CPU to another. All the remote I/O data was automatically transferred. It was a way to synchronize any other data between the two CPUs. But they are running identical programs so they should have the same data anyway. I never used this myself. To me it seemed unnecessary. But I'm sure someone can identify where they needed this.

This would be unnecessary in the ControlLogix. Synchronization of redundant systems is handled without the need for any logic messaging.

OG
__________________
I despise when people take random quotes and ascribe them to me - Julius Caesar
  Reply With Quote
Old July 30th, 2021, 03:30 AM   #9
koyeap
Member
Malaysia

koyeap is offline
 
Join Date: Feb 2013
Location: Selangor
Posts: 17
Dear Operaghost,

Thanks a lot for all the valuable info!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
RSLogix5000 to PLC5 Block Transfer Write scott.maddox LIVE PLC Questions And Answers 4 September 16th, 2015 10:21 PM
PLC5 Block Transfer Write RIO wevie0037@ LIVE PLC Questions And Answers 7 September 20th, 2013 12:35 AM
CoDeSys ST Function Block Call bopol LIVE PLC Questions And Answers 4 September 3rd, 2011 07:57 AM
AB PLC5 PID help bobbuilder LIVE PLC Questions And Answers 1 July 26th, 2010 12:06 PM
Ab Plc5 Rio Problem. fernandes LIVE PLC Questions And Answers 5 March 7th, 2004 02:25 PM


All times are GMT -4. The time now is 05:28 PM.


.