Do you mean "RIO" as the remote I/O protocol or as remote I/O?

Of course you can have I/O remote to the CLX rack. Using Ethernet I/P or ControlNet for example.
 
I might add, only EtherNet/IP or ControlNet.
For a CLX platform Universal Remote I/O communications, the remote chassis could be only 1747 (SLC), 1771 (PLC5), 1794 (Flex) or any other Generic Remote I/O hardware.
The OP is correct: you cannot Universal Remote I/O control a remote 1756 chassis.
 
The acronym "RIO" or just the phrase "Remote I/O" has a very specific meaning in the Allen-Bradley world; it refers to the 1980's vintage Allen-Bradley Universal Remote I/O protocol, and to the characteristic blue-jacketed cable that was used with that protocol.

This is the "blue hose" twinaxial cable that was used to connect I/O chassis and devices to the old PLC-2, PLC-3, and PLC-5 controllers.

This old technology doesn't have the speed or sophistication to carry the sort of data a 1756-series I/O module needs, so there is no "RIO Adapter" for the 1756 series chassis.

As mentioned above, ControlNet and EtherNet/IP are the protocols that are used to connect I/O chassis to the ControlLogix family controllers. No CPU is needed in the remote chassis, just a 1756 series network module like the 1756-CNBR or 1756-ENBT.
 
This old technology doesn't have the speed or sophistication to carry the sort of data a 1756-series I/O module needs, so there is no "RIO Adapter" for the 1756 series chassis.
Ahhhh, this explains it completely!! I was wondering how come you would need a PLC in the remote "control logix rack", I'm thinking to myself "sheesh, I am running PLC5 Remote I/O all day long with nothing other than an adapter module..." I never considered the I/O itself being more sophisticated and needing more data!!
Thanks Ken!
 

Similar Topics

HOW TO COMMUNICATE BETWEEN 2 ''EN2T'' MODULES MOUNTED ON THE SAME ALLEN BRADLEY CONTROLLOGIX CHASSIS. BUT TWO EN2T HAS DIFFERENT NETWORK. ONE EN2T...
Replies
7
Views
4,310
Hi, I have 2 x 1756-A13 Control Logix Chassis. What hardware do I need to connect them together? They will be located next to each other in the...
Replies
6
Views
1,657
we are converting PLC-5 controls with control logix system. The idea is to replace only PLC 5 processor and retain all existing PLC I/Os. Most of...
Replies
1
Views
5,338
I am having trouble with getting no control of my analog output signal. I am using the SCL function block to control my analog output. The logic...
Replies
11
Views
252
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
Replies
2
Views
379
Back
Top Bottom