olands Member O Join Date Oct 2005 Location Halifax Posts 1 Oct 6, 2005 #1 I have a A/B 1771-OA card that has enough leakage to keep a 120v solenoid powered. Should I add a MOV or simply replace the card?
jstolaruk Lifetime Supporting Member J Join Date Dec 2004 Location Detroit, SE Michigan Posts 3,912 Oct 6, 2005 #2 MOV won't help. Leakage for that card should be 2ma maximum. If its greater than that than I would suspect the card. Can you check it against the solenoid specs?
Gerry Member G Join Date Jun 2002 Location Auckland Posts 1,142 Oct 7, 2005 #3 Low power loads may need some parallel resistance to reach the minimum load spec. I haven't seen the problem with the 1771-OA but it was very common with the 1771-OM.
Contr_Conn Member Join Date Sep 2003 Location Ohio Posts 2,582 Oct 7, 2005 #4 Put 16K+/1w or 12K+/2W resistor in parallel with load. This will fix it. It's imortant to have in parallel.