analog output
panthripu
Mar 2004
228
hi
what program should i write to get 20 mA at output card when some internal bit/flag go high.I am using siemens s7-400.
Hope this helps, Daniel Chartier
Just in case the image can't be included, again:
In STL format:
A M232.0
JNB -001
L 27648
T PQW512
_001: NOP 0
When flag M232.0 is TRUE, MOVE (Load and Transfer) the maximum allowed analog value for Siemens analog modules (decimal: 27648)to the analog output channel you have configured (in HWConfig).
Hope this helps,
Daniel Chartier
Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
341
I have a 170AAO92100 card that I am interested in using as a 10 volt output. Is there setup that I have to do in order to change output or simply...
100
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
120
266
I have a program that I am gradually piecing together (my first program). There are 4 cascading timers that turn Y001 and Y001 + Y002 on and off...
552