CCW Micro870 - Modbus Communication
pml_28
Apr 2020
Brazil
Hello everyone,
I am trying to send/receive Modbus messages between two Micro870 PLCs using RS485 and 2x2080-SERIALISOL plug-in modules.
PLC1 - Hardware Settings
Baud Rate: 19200/Parity: None/Modbus Role: Master
Message Configuration:
Channel: 5 (installed in slot 1)
Trgger Type: 1
cmd: 3
ElementCnt: 16
Target Addr: 1
Target node: 1
PLC2 - Hardware Settings
Baud Rate: 19200/Parity: None/Modbus Role: Slave/Slave ID: 1
Trgger Type: 1
cmd: 16
ElementCnt: 32
Target Addr: 1
Target node: 1
However, on PLC1 (master), I get an error code 130 in the message exchange. I can't find what could be wrong. According to the Rockwell Automation documentation, Error 130 is a problem with the Modbus address, but it seems fitting. I have tried several address variations in the master PLC, for example: 4000, 40000, 400001, and it didn't work either. Does anyone have any suggestions as to what this problem might be?
Yes, you are correct. I configured the Modbus mapping, and the communication worked perfectly. I thought that that modbus mapping would only apply when using the controller's serial port. But I was wrong.
Thanks a lot. Solved. Cheers.
Hi shesame,
check in the CCW software > Controller section > Modbus Mapping. It is essential to create a Modbus mapping for your Modbus communication to function correctly.
Hi all. This is my first time working with the CCW software, and I'm using the CCW developer edition version 21. The PLC is a Micro870...
1,539
my ccw softwer stops working when i add and try to open a ladder program.
85
Hey out there, I am trying to build an alarm que in CCW. I have got the FFL and FFU working, however the string that goes with the alarm can't be...
38
512
Hello. Has anyone ran into an issue with HSC on 2080-LC20. It run a cut off press and every so often after resetting to 0 it does not count...
141
I am running CCW 13 trying to upload to a micro 820 vers.12 I get an output message OPC server is unable to load project controller. Please help!
298