Changing IP addresses
cornbread
Feb 2007
madison, indiana
407
I’ve been asked to help move some PLC’s & HMI’s behind a firewall. Part of the move requires assigning new IP addresses on SLC’s, PV+’s and compactlogix. In reading up on the subject I don’t foresee any problem. With that said, I’m hoping this learned forum can point any pit falls I may encounter or things I should look out for.
You most likely are using private ip address ranges now so why do you need to change them. Placing these devices behind a firewall does not require the addresses to be changed.
As jac said if there is a lot of messaging it could be involved if you are not comfortable with setting up messaging.
Any firewall worth having should have DHCP percistance,VLAN's and layer 3 routing. Sounds like the IT guy does not want to work.
Don't forget to look for any data transfers to other plc's or data collection systems. Also look for any apps such as wonderware, Rsview, ??? that get / use data, or access information from these plcs to signal other plcs what's going on.
regards,
james
Using studio 5000 with 1756-L71 and 1756-ENBT cards. Is it possible to change all IP Addresses that are being used for a plc, drives, enbt cards...
1,473
Hello, I recently changed the IP address of a Compactlogix L32E and an asssociated Panelview 1000. I can ping both of them so I know that the IP...
5,532
Hi, Today I was experimenting a little with TIA portal but I have a problem with changing the addresses of a DP slave. I've configured the CPU...
2,876
Hi. I was recently tasked with changing the IP addresses on 3 ControlLogix, 1 SLC 5/505, and 1 HMI computer(InTouch) on a working system...
3,521
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
236