Compactlogix IO Not responding
Ray S
Nov 2009
Ontario
37
I have a Compact logix L35E and a remote B&R X20B I/O system on a plant network that was working until we had to change the IP addressing because of updates to our network systems. Since the change i get an IO not responding fault on the L35E. I can ping the B&R from the L35E network line. The subnets are the same (255.255.255.0) however the devices are now on different gateways.
L35E IP 10.7.111.51 subent 255.255.255.0 gateway 10.7.111.10
B&R IP 10.7.121.125 subnet 255.255.255.0 gateway 10.7.121.10
Not sure this is why we get the fault.Thanks for any advice on this.
Is that connection setup as Multicast or Unicast?
Multicast connections will not route across gateways w/out further configuration on the Network end.
I have been having this error on the CPU Compactlogix L32Cwhich says that I/O are not responding . I checked in the minor faults and cleared...
2,119
I have a 1769-L33ER with several Danfoss drives set up as generic Ethernet modules. When I unplug a drive from the network, the "I/O Not...
2,661
I have a remote rack that has progressively gotten worse in giving me "I/O Not Responding" errors. Started faulting every couple days to today...
9,436
Hi to everyone, I am using a compactlogix 1769-L35E Rev 13.34 with 8 remote i/o racks. All of the communications is done via wi-fi using the...
3,165
128