Dear All friends,
I had trouble with Digi WAN 3G setting to connect with compactlogix PLC ( Rockwell).
I can't access to PLC over Internet.
Can you please advise me how to setting and connect with AB PLC if has experience for this.
I using Viet Nam mobile Network (3G)
Many thank,
 
First, be sure you are using the "Ethernet Devices" driver in RSLinx Classic.

The "EtherNet/IP" driver uses a broadcast packet to discover devices on the network. Broadcasts like that will not work over VPN, Internet, or routed networks.

Can you "PING" the device, or open its embedded Web page ?

A great tool for troubleshooting this kind of connectivity is called "TCPing". If you can use that to connect to TCP Port 44818, then you can move on to diagnosing what's going on with RSLinx Classic.
 

Similar Topics

Has anyone had similar issue? I have a digi one iap modbus tcp converter polling abs RTD data from pump controllers. I am new to the issue, but...
Replies
2
Views
1,460
I am replacing a Net ENI with a Digi IAP. I have been reading through the manual for the DIgi IAP and can see no information on how to get...
Replies
15
Views
7,513
I have a SLC 5/03 connected to an Ethernet network via a Digi One IAP. The IAP is configured to allow the 5/03 to READ from a SLC 5/05 through the...
Replies
4
Views
6,147
Greetings, I had an issue with a RIO rack 2 and IFM I/O Link dropping on my network. I would loose connection for a second or 2 then they would...
Replies
3
Views
114
Hi friends, i need a help to know the procedure and steps to connect Lenze i700 to PC for parameterize. i tried with lenze easy-starter using LAN...
Replies
0
Views
66
Back
Top Bottom