Does Inhibiting a module stops the scanner from scanning
bornwild
May 2010
Riyadh
429
Hello guys,
We a compact logix processor and one of the safety input modules 1734-IBS seems to be faulty as sometimes the module led turns red which causes a network fault. The inputs of the module are not used. Can I inhibit the module? Will it still cause the scanner to go in fault
I don't think you can disable any safety module
the communications to safety modules is handled differently the standard modules
if the communication is lost the safety controler will fault and turn off the safety controls
Think about it if a monitored safety input were to fai would you reall want the equipment to just keep running and hurt somebody
GaryS, I think you are right and I am wrong. The screenshot above is for a non-safety device. I just checked, the same screen for a safety device has the option "Major Fault On Controller..." greyed out.
To bornwild's answer, it should be possible to inhibit the safety device. Not sure if the fault in the PLC will not be genrated again once you clear the fault.
Hello guys,
Be aware of this from the Knowledgebase as you work on that problem:
"ID: PN1590 Product Notice 2022-05-001 - Allen-Bradley POINT Guard I/O 1734-IB8S/B, 1734-IB8SK/B Intermittent Connection Fault"
70
Hi, i am using DVP-14SS2 PLC, after program written to plc, when power is reset, plc doesn't run. always need to connect to pc for the run mode.
76
I am trying to connect with a Schneider plc which has a firmware version only available in Somachine v4.2. In Machine expert After taking upload...
140
They are installed in a control panel that was made in France and are intended for the termination of analog inputs. Each of the red capped...
451