Peter
I wish that I could use splines in the rockwell but all I have are CAM's
kamenges
You are correct, in the code there is a Motion Axis Move (MAM) that overrides the cam profile to return to position - I would not use it I'd just set the CAM up correctly - The shake that you are seeing in velocity during the MAPC is caused by the master reference being so coarse
Definitely - However on most systems that I have commissioned, by using Jerk I have been able to reach higher Accel's without the mechanical stress - I would not presume that curve to be for 69firebird until we know more plus I would change it for different lengths.Using s-curves is much better but there is a cost.
Agreed - that is his problem which he will be able to get around if he can get the system to be repeatable1. Calculating accurate speeds
I do not know about your system - In the rockwell look at the loop diagrams in http://literature.rockwellautomation.com/idc/groups/literature/documents/um/motion-um001_-en-p.pdf he is using the "Motor Position Servo" typeacceleration feed forward
Yes there is - Rockwell try to get rid of it by using Master Delay Compensation and I think that he has made it worse by using the master position filterThere is a time delay between the line speed encoder reading and the coarse update
kamenges