A new point I/O rack is to be hooked up with the running PLC. In point I/O, it is supposed to be the OA4 card to be installed as per the downloaded configuration in the PLC, but due to unavailability, can we install OW4 card or ARM module without restarting it and downloading the configuration again?
Welcome to the forum!
You can absolutely put an ARM module (or any other module) there and just inhibit the OA4 in the configuration. Inhibiting and uninihibiting can be done online and will prevent the PLC from trying to establish a connection to that module, and it therefore won't matter what it is.
If you actually need the outputs, you could potentially get away with using an OW4 in place of an OA4 if you had electronic keying for that module set to Disable. I've never tried and I wouldn't absolutely promise it would work, but it would be worth a shot. Unfortunately I'm 99.9% certain that changing that setting from the default "compatible module" to "disable" requires a download, so it's no better than just changing it to the OW4 in the first place.
Hello all, I am an Industrial Electrician, and deal with a little bit of everything including PLC troubleshooting and programming. When I started...
147
Hi Everyone, I am facing an issue while installing the STUDIO 5000 in my windows 10 PC. During installation I am getting an error that " Error...
186
During the process of installing Studio 5000 Mini Edition to my new machine at work, it seems as though some things like RSLinx Classic and the...
621
Hi All, I haven't installed Unity Pro in years and needed to install it recently. I initially tried installing Version 11.1 and the whole...
749
Hi all, I tried to install Twidosuite on windows 10 but after installing i have the registration link which is not working and also i get with...
599