Hello again, Bob
I was sorry to hear about your wife passing on. I know it must be very difficult to adjust, but keep on keeping on, and lean on your friends for support.
If you will ZIP your last RSLogix program and post it, I can probably come up with a start-up routine. The version that I have was called "Hershey Module R4.rss". looking at that program, I can see that if the Kissing Tower is manually turned off in the middle of a cycle, the PLC program will get out-of-sequence, since it depends on time and not totally on external sensors. It will not be difficult at all to add some PLC Inputs for Stop or Start pushbuttons. You may even want an external Master Control Relay, so that if the MCR becomes de-energized for any reason (loss of power, press of Stop pushbutton), then the PLC shuts off the program and resets the timers. That is considered the safest way to do an emergency shutdown, but since this is a model of some rides, not the real thing, you can prbably get by with an internal Master Control Relay, or System Run Relay, or something like that. Then you only have to add one rung of logic at Rung 0, like this:
| System Stop System Start Run Mode |
| I:1/4 I:1/5 B3:0/0 |
| | Run Mode | |
| | B3:0/0 | |
The Stop Pushbutton would be a Normally Closed pushbutton, and the Start Pushbutton would be a Normally Open pushbutton. If the Stop pushbutton is pressed, the seal-in contact B3:0/0 will drop out and the system will shut off. Any other safety switch or stop switch can also be add in series on the rung after I:1/4. You may want to add an input from your power supply, so that if power to the rides is lost, the PLC will shut down and reset the program.
The next step is to add the new Run Mode relay to all rungs where there is an output or timer. Just add an XIC instruction for B3:0/0 at the left side of each rung that needs disabling, which in your program may be all rungs. Then if Stop is pressed, or power is lost, everthing will shut down and the timers will reset.