The previous user might have attempted to load the incorrect Series firmware into the controllers, damaging them in the process.
This Forum member specifically asked if a PLC-5 Series C Firmware Revision D controller can be "flashed" to Firmware Revision E.2.
The specific answer is no, because there was never a Firmware Revision E.2 for the PLC-5 Series C controllers. There was a Firmware Revision E.2 for the PLC-5 Series D controllers, which are very similar.
The equivalent version for a Series C controller would be firmware revision N.2.
PLC-5 firmware revisions are not as easy as using ControlFlash on modern controllers. Rockwell Automation no longer sells a PLC-5 firmware upgrade kit for field use.
Instead, PLC-5 controllers can be sent through the Rockwell Automation remanufacturing process, during which they will be updated to the newest available firmware for their Series hardware.
For the 1785-L40B Series C controller, that will be firmware version U.2.
That's according to this RA Knowledgebase document describing the PLC-5 firmware revision history:
https://rockwellautomation.custhelp.com/app/answers/detail/a_id/18946
If there is a specific reason you need a firmware revision that is not the current release, you need to arrange that specifically with Rockwell Automation.
I am using the following formula and I am getting error, Invalid Expression - too many closing parenthesis. when i copy the formula to notepad or...
161
Preface: Kinda long, so I made section titles Intro: I just want to see if anyone here has seen anything similar. A PLC5-40 series C enhanced...
379
Hi, can anyone help me get a pdf file for this RSP files. They are from a PLC5. Thanks
532
Hello all, I am seeing this behaviour where an integer file (N46:33), has an integer in binary (11110) which is 30 in decimal. I did a...
525