I am working with a PLC5 in am 8 slot rack. 1771-A2B, in 1 slot addressing mode.
Rack configuration is:
Slot, R/G/S/C, Module Type, I.O/Point, Description
0 0/0/0/0 1771-IAD 16 120V ac 16PT INPUT
1 0/1/0/0 1771- OAD 16 120V AV 16PT OUTPUT
2 0/2/0/0 1771-IAD 16 120V ac 16PT INPUT
3 0/3/0/0 1771-IAD 16 120V ac 16PT INPUT
4 0/4/0/0 1771- OAD 16 120V AV 16PT OUTPUT
5 0/5/0/0 EMPTY SLOT
6 0/6/0/0 1771- IFE 16 12 BIT ANALOG INPUT (OR IFE/A
7 0/6/0/0 1771- IFE 4 12 BIT ANALOG OUTPUT
In the program I'm working on there are several references to inputs or outputs labeled I:050/7 or O:044/10. if the addressing is rack/group/slot with the group referring to the slot, in 1 slot addressing mode. What does the 44, or 50 refer to?
Which model of PLC-5 do you have? Most of them have a Remote I/O scanner port and can be connected to remote 1771 chassis and other devices on the old Allen-Bradley Universal Remote I/O network.
Rack numbers can go up to 77 (octal) but PLC-5 controllers typically supported 4, 8, 16, or 24 logical racks.
Hi
I would go along with ken.
If you check the front of the processor is there a blue cable or cables connected to a 3 pin connection. Just remember it may be another plc 5 rack, panel view, drive, flex I/o etc
Donnchadh
Thanks for the confirmation, clearly the engineering has not told me th hole story and I haven't seen the plant yet.
I am using the following formula and I am getting error, Invalid Expression - too many closing parenthesis. when i copy the formula to notepad or...
158
Preface: Kinda long, so I made section titles Intro: I just want to see if anyone here has seen anything similar. A PLC5-40 series C enhanced...
374
Hi, can anyone help me get a pdf file for this RSP files. They are from a PLC5. Thanks
526
Hello all, I am seeing this behaviour where an integer file (N46:33), has an integer in binary (11110) which is 30 in decimal. I did a...
522