power flex 40p, error code F005
heliocdw
Nov 2017
los angeles
hello everyone, i would like to explain my problem and see if someone can help me.
we have a machine to cut wood, original the aluminium head tolling where is placed the cutters , we replace for a metal head tolling, after that when we need to stop the machine the drive power flex 40p show on the display fault F005, the manual say MONITOR THE AC LINE FOR HIGH LINE VOLTAGE OR TRANSIENT CONDITIONS, BUS OVERVOLTAGE CAN ALSO BE CAUSED BY MOTOR REGENERATION, EXTEND THE DECEL TIME OR INSTALL DYNAMIC BREAKE,i increase the decel time but still the same problem, we put it back the aluminium head tolling and the machine works good with out any problem, but when we switch to metal head is when the faul pop up,,, thank you.
Any problem with letting it coast to a stop instead of ramping to a stop? If not, I would set it up to coast. It sounds like the weight difference of the metal vs aluminium is enough to cause to the motor to regen which is spiking the bus voltage.
If you can't let it coast to a stop, then you need to add an external brake to eat up the extra voltage.
Can anyone provide me with a AB cat # of a encoder that can be used with Powerflex 40P. The manual states that PowerFlex 40P will only works with...
2,157
Power flex 527 Network based safety drive had faulty and alarm pop up SOS Code internal fault Unable to set or clear the fault manually or...
143
Hi all. Would anyone happen to have the Modbus register datasheet for the Honeywell/EnergyICT EIMFlex Modular Meter v1.11 We've 40 of these that...
74
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
142
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
212