Rslogix 5000 Structered Text
peeka
Jan 2010
canada
IF Local:1:O.Data.0 THEN Local:1:O.Data.4:= 1;
END_IF;
for some reason I cant get the output (data.4) to turn on..... do I need to enable structured text for the plc at all ? I've just started to learn structured text as you can see.
I fell into a similar trap last week. I cut-and-pasted some simple code, then stared at it for over an hour before realizing the program didn't have a main routine specified.
You can just do:
Local:1:O.Data.4 := Local:1:O.Data.0;
Or
IF Output.0.Condition
THEN Local:1:O.Data.4 := 1;
Local:1:O.Data.0 := 1;
END_IF;
well, actually
B [:=] A;
is the equivalent of the rung construction XIC(A) OTE(B) ...
specifically, you need the [ ] square brackets to make the "non-retentive" equivalent of the OTE instruction ...
without the [ ] square brackets, the := assignment is "retentive" - like an OTL instruction ...
and we're only talking about Allen-Bradley's version of Structured Text as used in RSLogix/Studio 5000 systems ... it's different in the Structured Text used in the older PLC-5 family using RSLogix 5 ... and I have no idea how other manufacturers handle their "retentive" and "non-retentive" assignments ...
some additional material for those who might be interested can be found in the following thread from yesteryear ...
http://www.plctalk.net/qanda/showthread.php?p=529056&postcount=5
party on ...
well actually....
There are two aspects of OTL that are "retentive": that the bit remains true when the rung conditions are false, and that the bit remains true when "first scan" conditions occur.
OTE is wholly "non-retentive", in that the bit goes false if the rung conditions go false, AND it goes false when "first scan" conditions occur.
If A then B:=0 is truly non-retentive, as the bit remains set when both A = false AND on "first scan".
B[:=]A is truly retentive, as the bit becomes false when either A = false OR on "first scan".
B:=A is -- what? "semi-retentive" -- in that it acts like an OTE in how it responds to A (which was my point), but is immune to "first scan" resets (which is Ron's).
I would expect (though never tried it) that If A then B[:=]0 would be ¿quasi-retentive? as the B would be immune to A going false, but affected by first-scan. If so, it would be an "interesting" way of initializing a sequencer, provided one is an expert of when "first scan" applies, and when it doesn't.
I, for one, am not such an expert.
I'm trying to be "gentle" here (as I was in my previous post) ...
you are confusing "first scan" with "pre scan" ... they are not the same ...
Oh, don't be gentle. I've often said that posting here is the best way to learn, if you've got the stomach for it: posting something right is fine; when you post something wrong, you'll hear about it. And that's when you learn.
I had put "first scan" in quotes because I was thinking of pre-scan, but was having a bout of anomia and couldn't pull out the correct term. Thanks for keeping me honest.
108
208
I am completely stuck on building a ladder program that requires a start button to be pressed 3 times to turn on motor 1. Then motor 2 starts...
20
652
First off, I'm a hobbyist-level programmer, and this program isn't controlling anything anything that could even remotely be considered "life...
18
591