I came across a caveat in the Littlefuse whitepaper on this topic that says
“It is important to point out that step 2 modifications apply only to current-limiting devices in the feeder circuit with passive (non-overcurrent protective) devices in branch circuits. In this example, based on table sB4.2, the 60 ampere Ul Class J fuse in the feeder circuit is able to limit the ipeak to 10 ka or less if the available fault current were 100 ka. If there are overcurrent protective devices in branch circuits and the available fault current is less than 100 ka, but greater than the interrupting rating of the branch circuit overcurrent protective device, the branch circuit overcurrent device may begin to open before the feeder fuse clears the circuit, possibly causing a hazardous situation. Therefore, the SCCR of the panel cannot be greater than the lowest interrupting rating of any fuse or circuit breaker in the panel, unless it has been tested and listed by a NRTL.”