Wonderware DASIDirect v1.5.0 Intouch 9.5 to S7-1200

Join Date
Mar 2009
Location
Leeds
Posts
49
Can any one confirm for me that you can configure DASIDirect v1.5.0 to communicate to an S7-1200 over ethernet.
I've found reports of this working with DASIDirect v3.0 if you configure with the following settings. Set as S7-300 PLC with. Rack 0, Slot 1, connection resource 3, remote TSAP 3.

Also would it be be possible to at the same time have a KTP300 also connected via ethernet to the same S7-1200 PLC.

Thank you.
 
Rack 0 Slot 1 should work.
But you can only get access to "not optimized" data blocks (right click on the datablock which you want to access, and disable the option).
If you are using a 1200 with a newer firmware version, there is an option in the hardware config where you have to enable Put/Get communication to get this working. Older versions don't have this option, it's always possible.
 

Similar Topics

I migrated to a WSP2023 application. Now when I open a HMI object (for example a valve or motor) the popup is first correctly show as defined ...
Replies
0
Views
47
Hi guys, I have experience with PLC to Excel etc...just starting on using intouch scada screens. I have an Excel sheet that uses mainly...
Replies
1
Views
208
Hello everyone, Recently, my Archestra IDE shut down while I was editing. After restarting the IDE, I noticed warning symbols under my opened...
Replies
1
Views
131
Good morning all. I'm working on a rehab where they had a standalone InTouch 2014 HMI that they called a SCADA, but it's really basic stuff. The...
Replies
4
Views
218
Hi, We are setting up an Aveva Plant SCADA node with the intention to connect it to a Wonderware Historian node. Everywhere I look online I see...
Replies
1
Views
216
Back
Top Bottom