Hello I am trying to program a 3 position switch in wonderware. I believe that I have the animation set correctly in the HMI but, I am having an issue with the logic for this. Any help would be greatly appreciated.
 
Why are you doing the control in Wonderware?
Have the PLC do the control, and Wonderware do the animation based on the position as indicated by the PLC.
 
That is what I ended up doing. I am kinda new to the PLC end. I have developed HMIs before but never in wonderware. I have never written logic before but I hashed my way through it. Thanks
 