At the plant where I work, there is a centrifuge machine, 30Kw, on standard star delta contractors.
When there is a supply "blip" or voltage sag, the contactors "drop out", machine stops and causes havoc.
This machine has a lot of inertia, a heavy rotor i.e flywheel effect and travels at about 3,000 rpm so a couple of seconds freewheeling shouldn't cause it too much grief.
I have a Siemens Logo and a standard small PC UPS at my disposal.
My thinking was:
1. Supply the Siemens Logo from the UPS power output.
2. Use a relay output on the Logo, fed from the UPS output to supply the control voltage to the contactor circuit.
3. Use absence of mains supply as an input to the Logo to operate a 1 second timer, releasing the output. This output is in series with the machine stop circuit.
i.e.
If the mains supply is missing for more than 1 second the contactors drop out, requiring a manual start as per normal operation, but if mains supply is missing for less than 1 second then the contactors stay in.
Anything wrong with the plan ?
When there is a supply "blip" or voltage sag, the contactors "drop out", machine stops and causes havoc.
This machine has a lot of inertia, a heavy rotor i.e flywheel effect and travels at about 3,000 rpm so a couple of seconds freewheeling shouldn't cause it too much grief.
I have a Siemens Logo and a standard small PC UPS at my disposal.
My thinking was:
1. Supply the Siemens Logo from the UPS power output.
2. Use a relay output on the Logo, fed from the UPS output to supply the control voltage to the contactor circuit.
3. Use absence of mains supply as an input to the Logo to operate a 1 second timer, releasing the output. This output is in series with the machine stop circuit.
i.e.
If the mains supply is missing for more than 1 second the contactors drop out, requiring a manual start as per normal operation, but if mains supply is missing for less than 1 second then the contactors stay in.
Anything wrong with the plan ?
Last edited: