At the plant where I work, there is a centrifuge machine, 30Kw, on standard star delta contractors.
When there is a supply "blip" or voltage sag, the contactors "drop out", machine stops and causes havoc.
This machine has a lot of inertia, a heavy rotor i.e flywheel effect and travels at about 3,000 rpm so a couple of seconds freewheeling shouldn't cause it too much grief.

I have a Siemens Logo and a standard small PC UPS at my disposal.

My thinking was:

1. Supply the Siemens Logo from the UPS power output.

2. Use a relay output on the Logo, fed from the UPS output to supply the control voltage to the contactor circuit.

3. Use absence of mains supply as an input to the Logo to operate a 1 second timer, releasing the output. This output is in series with the machine stop circuit.

i.e.

If the mains supply is missing for more than 1 second the contactors drop out, requiring a manual start as per normal operation, but if mains supply is missing for less than 1 second then the contactors stay in.


rurv9w.jpg


Anything wrong with the plan ?:)
 
Last edited:
Your concept of supplying the plc and machine contactor with a separate UPS is good to eliminate the nuisance dropouts. There "may" be an issue with generated back voltage from the freewheeling motor or maybe not. It depends on residual magnetism in the motor and a few other things like inductive phase shift and so forth. That probably won't be a problem but just want you to be aware if you get some unexplained fuse blowing or circuit breaker tripping on the mains shortly after the power resumes from the "blip". I based my reply on your description of events, I didn't review your logic symbols because I am not that familiar with them.
 
Last edited:
There are standard capacitor hold-up units that can attach to the coils to maintain them during dips, specifically for this purpose. There are several other technologies that can do this too, without the need and maintenance of UPS batteries, which WILL eventually fail. Look up a Dysc system made by SST (Soft Switch Technologies)
 
You might also want to find out why you are getting voltage sags. Stopping the sags would seem like the absolute best solution.
 
Thanks for the replies.

First of all, nothing we can do about the voltage sags/drop out's. This is up to the supply company and their recliner systems i.e not going to change.

Second point is these machines are fed from different panels, not in proximity to each other, so small portable solution is best. We have loads of little ups units, which would fit in a panel and also are cheap, so I guess I will try one and see what happens.
 
Thanks for the replies.

First of all, nothing we can do about the voltage sags/drop out's. This is up to the supply company and their recliner systems i.e not going to change.

I'm not familiar with the power supply company term 'recliner systems.'
This was my first thought.
homer.jpg
 
That's because autocorrect changed "recloser" to "recliner" :D
iOS devices will also correct "contactor" to "contractor" every time. So it's conceiveable that if you wanted to discuss a "recloser contactor" it might come out as "reclining contractor". That Homer image becomes even more appropriate...
 

Similar Topics

Hello all- I have a unique challenge using a customers Direct logic 06 PLC. This customer has a DC motor operating at 10 RPM which is turning a...
Replies
1
Views
136
I've got 6 identical regenerative vacuum blowers powered by 6 identical drives in 3 identical panels all fed from the same 1 main building feed...
Replies
27
Views
878
Hi all, We are currently experiencing an DC over voltage fault on one of our inverters. During commissioning a snag was raised whereby excess...
Replies
0
Views
199
I have a Siemens 1515 controller with the configuration of cards (input, output, safety input, safety input, safety output). I am having an issue...
Replies
2
Views
180
Good Morning , I installed an AC Tech ESV 1 HP Drive on a small bucket conveyor. Before it had a DC Motor on it . It now has a Baldor 1 HP...
Replies
1
Views
209
Back
Top Bottom