Is it possible to have a MicroLogix 1400 read information from a CompactLogix address?

I've done it the other way many times. Reading the data tables of a MicroLogix plc with a CompactLogix, very simple.

But I'm looking through the MSG instruction in RSLogix 500, and am not sure which if any of these communications commands will work, or if I have to structure the data in the CompactLogix a certain way.

Edit: The plan is Ethernet communication, if that makes any difference

Thanks
 
Last edited:
You'll have to map some addresses in the Compactlogix to registers the 1400 can read and write to. In Logix/Studio 5000 this option is found under the "Communications" menu and does require a download.
 
Hope this will help you.

Somewhat, but that Step 3 "Target Device". The Data Table Address field (if it's a 500CPU Read that is used?). That's the part that wasn't very clear.

bjh said:
You'll have to map some addresses in the Compactlogix to registers the 1400 can read and write to. In Logix/Studio 5000 this option is found under the "Communications" menu and does require a download.

Ok, I think I found what you are getting at. Is it the "Map PLC/SLC Messages..." option under the Logic menu?

So I can just make the CompactLogix mimic a SLC and use a 500 Read/Write in the MicroLogix to those addresses?
 
So I can just make the CompactLogix mimic a SLC and use a 500 Read/Write in the MicroLogix to those addresses?

Yes. I like to use an array of INTs. Say you have an array called "Micro1400_Read" with a size of 256 mapped to the SLC 70 datafile. Then the ML1400 can do a message read of N70:0 and up which will map to Micro1400_Read[0], N70:1 will be Micro1400_Read[1] and so on.
 
Ok. I understand it now. Thanks.

One of those things where I didn't even know where to start looking. Didn't know about the PLC5/SLC Mapping function of the Compact/ControlLogix.
 

Similar Topics

Hi all I'm trying to setup a MSG connection (which I'm not familiar to) between a CompactLogix CPU (L310ER) and a Micrologix 1400 CPU. At the...
Replies
1
Views
816
Hey guy's. I'm doing a Micrologix to Compact Logix conversion and ran into an issue with a COP command. My source in 500 is #N[N7:40]:0...
Replies
1
Views
734
Hi all. I know it is late in the day on Friday but I am stumped on something. I am doing a string transfer via messages from a CompactLogix L24ER...
Replies
16
Views
4,786
Hi everyone, Brief overview of the issue: I have a CompactLogix (pt No:1769-L36ERM) that is connected to a MicroLogix 1400 (Pt no: 1766-L32BXB)...
Replies
9
Views
4,306
Hello Everyone, I am trying to pull a few data table points from a MicroLogix 1400 L32AWA Controller into a CompactLogix L30ER over ethernet. I...
Replies
2
Views
1,611
Back
Top Bottom