Christoff84

Lifetime Supporting Member + Moderator
Join Date
Jun 2006
Location
Cambridge, ON
Posts
407
Hey folks,

I'm betting this has been answered a few times but I can't seem to find the answer.

I've setup a control logix gateway (1756-ENBT/A, 1756-DHRIO/C x2) to communicate with my PLC network (All SLC 5/04) over ethernet. The PLC network behind the gateway is DH+ (57.6K).

My problem is that I can not upload/download to my panelview 550s over the ethernet. The models are 2711-K5A5 running firmware 2.xx and connected to the PLC via the serial port setup for DH-485.

I believe the problem is located in RSLinx v2.43, I can pass-thru to see the DH485 (Chan 0) on the PLC but nothing on the other side of it (The Panelview). I've always had to plug directly into the DH+ network to upload/download via a PCMK card.

If anyone knows how to solve this any help would be greatly appreciated.

Chris.
 
Not COMPLETELY the same problem...but very similar...

This has happened to me before. I started or joined another thread that investigated this very issue.
In short, I had to connect to the DH+ port on the RIO/DH+ card with the PCMK-B card/cable combination. You can download successfully that way.
If you browse the LG5K rack in Rslinx, you can actually drill down to the PV550 with ease. In Panelbuilder, you can start a download using the passthrough Rslinx option. The problem is, about 3/4 of the way through the download the transmission fails.
I will look for my posts and reply again.
This is a common problem....

Here is the link





Application Note




A19584 - Gateway Passthrough Downloads now enabled in PB32: ControlLogix Ethernet to DHRIO DH+ Standard PanelView
Previously Released as #13559

Link
Product Category:


EOI
Product(s):




PanelView
Catalog #s:




2711ND3
Series / Revision:


On Internet


Status: Released on 02/28/2003 (Modified on: 02/28/2003)
Topic (Keyphrases):




communication, downloads, enet, software
Summary of Technote Information:



REQUIREMENTS

USING 1756-ENET card...
1. PanelBuilder32 software V. 3.61 or above.
2. RSLinx software V. 2.20.01 Build 107 (SP1) or above.
3. PanelView firmware 4.10 or above.
4. 1756-ENET card firmware:
Ser. A: running 1.18, or 2.6 or above (does not work with 2.01)
Ser. B: running 2.6 or above (does not work with 2.01)
5. 1756-DHRIO card firmware 2.17 or above

USING 1756-ENBT card...
1. PanelBuilder32 software V. 3.80 or above.
2. RSLinx software V. 2.40.01 Build 16 or above.
3. PanelView firmware 4.10 or above.
4. 1756-ENBT card firmware 1.40 or above
5. 1756-DHRIO card firmware 2.17 or above




Documents Requiring Click-Wrap Agreements:

Attachment Name Attachment Size
Gateway Download - Ethernet to DH+ for ControlLogix.doc 167,424


Search keywords: Passthru, Passthrough, pass thru, pass through, enet, ethernet, dh+, dhplus, dh plus, data highway plus History and Comments: 02/07/2001 Jerodd E Jones - Created this technote
09/21/2001 - Last update as RA Knowbase Doc
11/5/01 - Technote imported into combined Knowledge Base from RA Knowbase Doc
11/5/01 Agent Modified - Added General Category EOI. Replaced product family 2711 (Standard Panelview) with PanelView.
11/13/01 - Agent modified - Status changed from Draft-New to Released, Internal Only
2/14/2002: Previously released Technote modified by Jerodd E Jones.
02/15/2002: Released by Ken E Brown.
7/26/2002: Previously released Technote modified by Jerodd E Jones.
07/29/2002: Released by Ken E Brown.
8/19/2002: Previously released Technote modified by Jerodd E Jones.
08/20/2002: Released by Ken E Brown.
2/26/2003: Previously released Technote modified by Jerodd E Jones.
02/28/2003: Released by Mike S Moskin.


Edit Information: Assigned To: Additional Authors: Author: Jerodd E Jones Author Name: Jerodd E Jones/Cleveland/RA/Rockwell Date Created: 02/07/2001 Original Publish Date(s): 09/21/2001 02:58:51 PM
02/15/2002 03:30:34 PM
07/29/2002 11:12:25 AM
08/20/2002 03:41:42 PM
02/28/2003 01:23:25 PM
Most Recent Publish Date: 02/28/2003 Last Modified Date: 02/28/2003


Reviewer: Thomas R Upham/Mequon/RA/Rockwell
Mike S Moskin/Cleveland/RA/Rockwell
Ken E Brown/Cleveland/RA/Rockwell
Dennis M Wylie Jr/Cleveland/RA/Rockwell
Robert B Meeker/Cleveland/RA/Rockwell
Mark Hulland
Chad A Burks
Scott K Allan
Jose L Sanchez
David M Jimenez
Lianne A Wong
Mirela Cunjalo
 

Similar Topics

I have been trying to add a button to an HMI Panelview version 5.1 for a couple days. Each time I download I get no data in my buttons, only...
Replies
0
Views
219
Hello, I have a machine with a 1756-L72 Controllogix PLC and 1756-EN2T network card, and PanelView Plus 7 HMI. I am using RSLogix V20.05.00...
Replies
12
Views
967
Got a problem on an install this weekend I'm hoping someone can help out on. I'm upgrading an old system with a SLC5/04 and Panelview 600...
Replies
3
Views
1,163
Hello. At work we've acquired an old tubing end former machine we're trying to get running. The machine came with 2 floppy disks that have .RSS...
Replies
26
Views
5,720
Good Evening , I added a few screens to a FactoryTalk View ME Application, I'm going to download this modified application to the same...
Replies
4
Views
2,576
Back
Top Bottom