Help in upgrade of Micrologix 1500

gado

Member
Join Date
Aug 2007
Location
Legaspi City, Albay
Posts
6
Dear All,

Need your inputs as how am i going to upgrade my present system. I want to add two(2) to three(3) 1769-OW16 Output Relay modules.

My present system consist of the following:

Slot # Part # DEscription
0 Bul. 1764 Micrologix 1500 LRP Series C
1 1769-OW16 16-Output Relay
2 1769-IR6 6 Channel RTD Module
3 1769-IR6 6 Channel RTD Module
4 1769-IR6 6 Channel RTD Module
5 1769-IA16 16-Input 79/132 VAC
6 1769-IA16 16-Input 79/132 VAC
7 1769-OW16 16-Output Relay

One thing more, my power supply loading says it's overloaded.

What shall i do? Help please.

Gado
 
gado said:
Dear All,

Need your inputs as how am i going to upgrade my present system. I want to add two(2) to three(3) 1769-OW16 Output Relay modules.

My present system consist of the following:

Slot # Part # DEscription
0 Bul. 1764 Micrologix 1500 LRP Series C
1 1769-OW16 16-Output Relay
2 1769-IR6 6 Channel RTD Module
3 1769-IR6 6 Channel RTD Module
4 1769-IR6 6 Channel RTD Module
5 1769-IA16 16-Input 79/132 VAC
6 1769-IA16 16-Input 79/132 VAC
7 1769-OW16 16-Output Relay

One thing more, my power supply loading says it's overloaded.

What shall i do? Help please.

Gado

add an expansion I/O bank with a power supply


m1500_upgrage.jpg






Ian
 
Last edited:
Dear curlyandshemp,

Below are some data for my processor.

OS Catalog No. S:57 = 1510
OS Series S:58 = C
OS FRN S:59 = 9.0
Processor Cat. No. S:60 = 1764-LRP
Processor Series S:61 = A
Processor FRN S:62 = 2.0

Please advise if what are the things to be change in order for me to add an expansion powersupply and maybe three(3) output relars.

Thanks,

gado
 
gado said:
Dear curlyandshemp,

Below are some data for my processor.

OS Catalog No. S:57 = 1510
OS Series S:58 = C
OS FRN S:59 = 9.0
Processor Cat. No. S:60 = 1764-LRP
Processor Series S:61 = A
Processor FRN S:62 = 2.0

Please advise if what are the things to be change in order for me to add an expansion powersupply and maybe three(3) output relars.

Thanks,

gado

You should be OK



morE_M15001.jpg




m1500_parts.jpg
 
Dear curlyandshemp,

Thanks for the info. Which among the power supply listed (1769-PA2, 1769-PA4, 1769-PB2, and 1769-PB4) would you recommend for my purpose? I will add three(3) 1769-OW16 relay output modules. How will i verify the VERSION of my programming sofware?

Please advise.

Thanks and regards,

gado
 
gado said:
Dear curlyandshemp,

Thanks for the info. Which among the power supply listed (1769-PA2, 1769-PA4, 1769-PB2, and 1769-PB4) would you recommend for my purpose? I will add three(3) 1769-OW16 relay output modules. How will i verify the VERSION of my programming sofware?

Please advise.

Thanks and regards,

gado

Rslogix version, select Help --> About Rslogix 500


rslogix_500_ver.jpg



Power supplies, either the 1769-PA2 or PA4 will do
I usually use the PA4


power_supplies.jpg
 
Dear curlyandshemp,

Alomost everything are checked and i think im on the right track now except for the minimum length of cable i need. Due to the limited space in the control panel, my expansion bank needs to be installed a bit far from the existing bank. I measure it and i will need at least 6 feet of cable.

Advise please.

Regards,

gado
 
gado said:
Dear curlyandshemp,

Alomost everything are checked and i think im on the right track now except for the minimum length of cable i need. Due to the limited space in the control panel, my expansion bank needs to be installed a bit far from the existing bank. I measure it and i will need at least 6 feet of cable.

Advise please.

Regards,

gado

The documentation clearly states, the choices for cables are 1 foot or 1 meter, those are your two choices. If you want this to work, then you need to figure out how to position the expansion rack within 1 meter.

Only other option is a Devicenet scanner added to your main rack and compact I/O blocks on devicenet for the expansions
 

Similar Topics

Hello everyone! I'm currently working with SIMOTION D410-2 with a CF Card labeled with SIMOTION D410-2 V5.3 SP1 HF9 + SINAMICS V5.2 HF6 From...
Replies
2
Views
537
First a little backround. My company has 7 pieces of equipment from same manufacture. 1 newer model roughly 1 year old with a compactlogix PLC...
Replies
34
Views
10,991
Hello all! I am in need of the V21 firmware upgrade for the L33ER compact logix processor. I recently upgraded to V21 Studio 5000 and the program...
Replies
2
Views
3,766
Equipment manufacturer sent an upgraded program file, but I cannot open it with my version of CX-Programmer (Version 6.11). It says I have to...
Replies
1
Views
2,859
Hi all, I'm desperately trying to upgrade all our factory PLCs to S5. We used to have S7 PLCs (mostly 315 PN/DP) but we were finding them...
Replies
9
Views
2,679
Back
Top Bottom