I hope this makes sense, It's 3:15am and I'm really frustrated...
Here is what I have:
PowerFlex 400 VFD w/22-COMM-E Ethernet board.
CompactLogix 1769-L32E Processor
H-O-A switch
Relay(we'll call it R1) w/2 form C contacts that is energized when HOA is in Hand.
Right now there is a NO contact from R1 going to the drive's Start terminal (02) and a NC contact from R1 going to terminal 8 (Set to default "Comm Port") telling the drive to use Comms when HOA is not in Hand.
Here is what I'm trying to do:
When HOA is in Auto I want the start command/speed reference to come from the PLC over Ethernet. This part works fine.
When HOA is in Hand and VFD-PLC Comms are OK, I want the start command to come from drive terminals using R1 and the speed reference to come from PLC. I could change the PLC program so the start command still comes from the PLC if I need to but....
Most importantly, when HOA is in Hand and Comms have failed, I want the start command to come from the drive terminals using R1 and the speed reference to come from the drive keypad. In other words, when I put the HOA in Hand I want the drive to start and use the arrow keys on the keypad to control speed. I can't seem to find a combination of drive inputs and parameters to do this. The drive is set to Stop instead of Fault on Comm Loss (param C105). Am I asking too much? Is this even possible?
Thank you for your time.
Here is what I have:
PowerFlex 400 VFD w/22-COMM-E Ethernet board.
CompactLogix 1769-L32E Processor
H-O-A switch
Relay(we'll call it R1) w/2 form C contacts that is energized when HOA is in Hand.
Right now there is a NO contact from R1 going to the drive's Start terminal (02) and a NC contact from R1 going to terminal 8 (Set to default "Comm Port") telling the drive to use Comms when HOA is not in Hand.
Here is what I'm trying to do:
When HOA is in Auto I want the start command/speed reference to come from the PLC over Ethernet. This part works fine.
When HOA is in Hand and VFD-PLC Comms are OK, I want the start command to come from drive terminals using R1 and the speed reference to come from PLC. I could change the PLC program so the start command still comes from the PLC if I need to but....
Most importantly, when HOA is in Hand and Comms have failed, I want the start command to come from the drive terminals using R1 and the speed reference to come from the drive keypad. In other words, when I put the HOA in Hand I want the drive to start and use the arrow keys on the keypad to control speed. I can't seem to find a combination of drive inputs and parameters to do this. The drive is set to Stop instead of Fault on Comm Loss (param C105). Am I asking too much? Is this even possible?
Thank you for your time.