Airborne87
Member
Has anyone had the devicenet module not hold its configuration? This module has been in use for one month I was called in for a machine down situation. I have tried many times to download the configuration.
Another way to determine which device's connection has a problem is to check the Device Status array in the 1769-SDN Status connection to the CompactLogix.
The address will be similar to: Local:1:S.DeviceStatus[x] where x is the node number of the slave device.
A method for troubleshooting Error 77 problems is described in the RA Knowledgebase Answer ID # 24919.
If you can upload whole network configuration (or at least the 1769-SDN and the affected slave) and post the RSNetworx for DeviceNet *.DNT file, I or other Forum members can probably point to the problem.
Thanks for the answer I.D., Ken, but, sadly, that information is so important its locked up!! (Wonder what it did wrong?)
These are your only options when using a ML1500 processor to my Knowledge you cannot 'bridge' from the ML1500 to the scanner, like you can with the SLC500 and PLC5 processors.