CLX node loss fault

frw312

Member
Join Date
Jun 2005
Posts
85
I have a CLX system with multiple nodes on ethernet. If communcations to one or more nodes is lost then the plc faults and shuts doen the entire plant. Is this a configuration error or is there a way to mask out the faults so that the system doesn't shut down? Thanks for any suggestions.
 
If you open each node in Logix5000 and look at the connection tab there should be a checkbox for "Major Fault On Controller if Connection Fails While in Run Mode". Uncheck this to stop a node loss from faulting the processor.