i have a customer with an existing AB1200 that has a RS232 panelview attached. It (the 1200) has some spare I/O and the customer would like me to extend the current program to operate 5 new valves in another part of the building. He needs limited OIT capability in the new setup and i could provide user input with a few pushbuttons, but i need to have the PLC echo some readings back onto some kind of display with characters. The 1200 does not appear to support a 2nd OIT. Can anyone recommend a solution?

narlin
 
Without totally answering my own Q?, I could add a 1761-NET-ENI which should allow for an ethernet address and thus communication to another net device. So what is an inexpensive e-net display device for use in another room? Also, with the Ethernet addition, could the additional device be a full OIT to talk back and forth in additionto the existing panelview?
 
Yes, the NET-ENI would allow you to replace both HMI devices with ethernet capable devices.

In order to keep the functionality of the existing serial Panelview, I think you would need a Digi One IAP (which is like the NET-ENI but with two configurable serial ports not limited to Allen-Bradley protocols).

Please provide catalog number of your existing PanelView.

Other options would be to:
a) use DH485 and a NET-AIC (or 2 or 3) and switch the existing Panelview protocol to DH485 (if possible).
b) Add a gateway device like a Red Lion G3 and make it the ethernet bridge and 2nd HMI
c) serial port splitter (not sure what the limitations would be).

Keep in mind that ethernet comms through a serial port can't speed up the serial port! So once you get the devices on Ethernet, be sensible in how much data you try to remotely access and keep it organized.

To add specifics, I think we need to know the physical distances between devices (existing and proposed) and the catalog numbers of the PLC and existing HMI.
 

Similar Topics

Hi Guys, I am trying to establish communication over profinet between Siemens S7-1200 PLC as IO device and codesys plc as IO controller. But I am...
Replies
43
Views
2,859
Which signals do I have to use to get data from camera. For example camera detects a defect and sends signal to controller. Power cable: CCB-PWRIO-05
Replies
1
Views
213
can i send and recieve data using my yokogawa UT35A controller with my siemens s7 1200 plc using profinet communication without using gsd file
Replies
1
Views
383
Good day, everyone, We're trying to establish an S7 connection on ethernet between an S7-400 CPU and a new S7-1200 CPU (which is defined as slave...
Replies
10
Views
2,622
I don't have any prior experience with MicroLogix so the Communication Toggle Button is new to me. We currently have a few MicroLogix that are...
Replies
4
Views
2,217
Back
Top Bottom