Hi gentlemen! I need some help. I have a MicroMaster430 with profibus module. As is described in first step manual I reset to factory settings and configured adress in P0918 and on DIP switches. I also configured parameters P0700,P1000 = 6 - full control from profibus. I use Microsoft Starter sowtware, and CP5512 module. PG/PC interface is configured as Profibus with 187,5Kb/s, cable used is standard profibus cable with simens connectors. When i try to find Micromaster (diagnostic in PG/PC interface) computer doesn't find it, i also tried Starter option - but also with no results. What can be problem ?
 
I'm an semi-old man, but still I don't remember ever trying to connect as you do, without a controller.

Did you try to connect directly to the MM, with the CP5512 original cable only?

And what node numbers do you use?

Kalle
 
Your connection will work. I connect 5512 directly to
MM4 all the time.
So two things
Check cable because under pg pc you should see the
Drive address

If not then check cable again :)
Just use a standard profibus cable
 
Your connection will work. I connect 5512 directly to
MM4 all the time.
So two things
Check cable because under pg pc you should see the
Drive address

If not then check cable again :)
Just use a standard profibus cable
Hi JRW, the cable works with CPU313C-2DP as well MPI as ProfiBUS. The problem is not in cable. I don't find the solution of this issue, I aslo tried 1: to change profibus module, 2: I supplied module with own source of +24V still no results.
 

Similar Topics

hello guys. I'm using 5 Stratix 5700 Switches 4 of them make DLR(Device Level Ring) And one of them software version is not matched 15.2(6)E1...
Replies
2
Views
2,296
Good evening/day... I have a PV550 ( 2711k5a9L1 - frn 4.11) and i have a several problems with connections between panel and PC ( pc have a com...
Replies
5
Views
4,984
Hi all, Not the way I would like to splash the board, but we are in need of some simple assistance... I have an MD29 card on our Master Drive unit...
Replies
15
Views
9,737
Hello, We have a Sinamics S110. A while ago we had some troubles with drivecliq and we even needed the assitance from Siemens experts. It was the...
Replies
3
Views
5,744
I have Ge Fanuc 90-30 and Inet PLC , i want Connect by PME 6, i use cable which is working on another Ge Fanuc ,, The problem that after i...
Replies
17
Views
11,842
Back
Top Bottom