curlyandshemp
Lifetime Supporting Member
On a job site , where we have 2 460/480 stepdown transformers. Once supplies 120 VAC for controls(1,5KVA), other supplies 230 VAC (3KVA)for an MCC panel air conditioner. Plant 480 is actually sitting @ 500VAC, but customer has noted other 460/480 feed controls have been operating for years with not issues.
Tonight, the fusing to both of the step down transformers blew on MCC panel powerup. Fusing amps has been properly calculated and all week had no trouble until today.
Only way I could get my 460 / 120 VAC transformer to stop blowing fuses was to up rating from 3a to 6a. Unfortunatley I have no larger fuses than 6a . The 3KVA transformer had 7.5a fuses, and even with no load, the 6a blow. Primary ohms and secondary ohms all check out ok. No leak between primary and secondary. Today was unusually hot in the plant.
We are using Bussman Low Peak Class CC fuses ( time delayed ) to protect both transformers, part # LP-CC-XX xx=current . Am I using the right type of fuse for thes transformers.
Tonight, the fusing to both of the step down transformers blew on MCC panel powerup. Fusing amps has been properly calculated and all week had no trouble until today.
Only way I could get my 460 / 120 VAC transformer to stop blowing fuses was to up rating from 3a to 6a. Unfortunatley I have no larger fuses than 6a . The 3KVA transformer had 7.5a fuses, and even with no load, the 6a blow. Primary ohms and secondary ohms all check out ok. No leak between primary and secondary. Today was unusually hot in the plant.
We are using Bussman Low Peak Class CC fuses ( time delayed ) to protect both transformers, part # LP-CC-XX xx=current . Am I using the right type of fuse for thes transformers.