It depends. Are the wires run parallel to each other in the same conduit instead of just crossing perpendicular to the alternating source? What are you reading the thermocouples on? What are the readout's specifications for noise rejection? Have you looked at the thermocouple's output on a oscillascope (i.e. do you see a sine wave/ what makes you think it is a problem?) Does the reading on the thermocouple change at a steady state temperature condition if the 15-20 VAC source is shut off?
 
Hi. Im not sure how the power cables are run besides the thermocouple leads. the thermocouple is in a duct which is insulated, which is used to measure the temperature of our fuel line which has elements in. to maintain the fuel temperature. so basically the thermocouple is connected to a stand alone controller which switches the coil voltage to bring in the elements.the current temp reading is 15 deg and has 15-20 VAC on both the positive & negative leads,with respect to earth and that doesn't seem correct to me. i tried bridging the negative lead to earth, that got rid of the VAC to +- 200mV but controller still indicates 15 deg of the fuel line. i simulated a mV output into controller, and it works fine.

one more thing, the other thermocouples are working fine with no interference on them.

Unfortunately i can't remove thermocouple from the line because of its installation to test it on an oscilloscope and i don't know the noise rejection spec either, i have never experienced this before.
I initially thought that because there is a lot of interfere on the leads, its suppressing the mV output, therefore wrong indication of 15 deg, bt when i got rid of that interference, it remained the same.
 
Last edited:

Similar Topics

I am having an issue getting a IY4 to read my thermocouple correctly. We have a R type and K type hooked up and sitting at a known room...
Replies
5
Views
528
Posted by u/mr_biodtox 44 minutes ago Delta ISPSoft - Establishing communication with thermocouple module Hi, How do I establish communication...
Replies
1
Views
337
Hi, We have an ongoing project with a lot of thermocouple involved that monitor the temperature of heaters. There are more than 20 PID...
Replies
32
Views
3,473
Hello. PLC beginner here, so apologies in advance for any incorrect terminology or poor communication. I have an SLC 500 Thermocouple/mV Analog...
Replies
1
Views
649
Hello Guys, Trying to scale a thermocouple directly into my IY4 card. Connected into the terminal +\-. I’ve scaled the range of my J type to...
Replies
4
Views
1,663
Back
Top Bottom