Hey guys,

So im currently programming a sequences for my pump logic for a project. I have tested the program and so far its "full proof"🍻. However i am aware of the infamous "Go to Run" Conditions (courtesy to Ron Beaufort) such that if the PLC's losses its power, if some operator, switch the mode of the plc from run to remote, or from run to program then run, etc.

So i currently have a 1756-L62 5562 control logix plc which iam testing this on, and im trying all possible scenario's. so let me know what you guys think of other ways to test the "Go To Run" conditions.
 
There are only two ways to command the CPU to "Go To Run".
One is via controller Mode Key switch (turn to Run or Remote Run positions).
The second is via Online RSL5K software, presuming that the CPU Mode Key switch is in the Remote Run position and the software commanded the last switch from Run mode.
There isn't much testing to be done unless trying to Emulate the application prior to "turning it loose" on the controller.
You will eventually have to run your "fool proof" application on a CPU...What could possibly go wrong?!...:D
Try isolating the output's power supply and monitor the "running" logic without "making decisions" in the field.
 
The RSLogix 5000 also has a "Test Mode". This will run the logic, but the actual outputs are disabled.
 
It was only a suggestion after all...:D
Complex applications might need to be "emulated" prior to CPU deployment.
For a simple application (I presume it's the Cooling Tower), once the I/O has been thoroughly identified and verified against the programming logic and if the developer is acutely aware of the consequences of any "malfunction" just a "Test Mode/outputs off" monitoring might be sufficient.
 
@ Jkerekes the test mode is pretty useful when testing prior to using your actual outputs, my plc that i'm currently using has a bad battery so if i remove power to the plc while the plc is running and then put power back on it loses its program. The reason why im mentioning this is because i'm trying to simulate what would happen if a power loss occured while the plc was running and what would result if power resumed, im assuming that would be treated as a Go to Run condition, but i could be wrong, let me know what you guys think.
 
If you have concerns about the way the CPU "wakes up" after a power failure you might want to consider the RSL5K Power-Up Handler feature.
This capability allows the user to logic program define the way the system returns to functionality after losing control power while in Run/Remote Run Mode.
 
Last edited:
@dmargineau, ok but without using the Power-Up handler, i just want to know what happens when power to the plc is lost will it was running then all of the sudden the power is resumed, depending on that answer i may or may not need to have a power-up handler.
 
Depending of the hardware used, most of the available output modules' "actions" are configurable within a Safe State mode; this could also be used in case of control power or "master" communications loss.
 
@ demargineau ok thanks, @ JHarbin lol, of course their is no such thing as full proof i totally agree with that, you would be surprised by how many "gotcha's" i found in the program
 
@ OkiePC i just had this talk with my colleague today, he was describing pretty what you said an operator will find a way to lock up your system no matter how well you program lol, i was on a service call yesterday and to start a system all you need to do is meet you permissives and hit the start PB "once", however this operator almost always hot it more than 3 times, i asked him why and his reply was "i just want to make sure it comes on" meanwhile in the logic all hell is breaking loose operator's i tell ya
 

Similar Topics

I have a system that is using TCP sockets. There are 5 connections between the Ethernet card and the end devices (smart conveying system)...
Replies
0
Views
698
Hello to all peers & Allen Bradley brainiacs, (not me)! My title is long but it pretty much says it all. The subject controller uses all 1756...
Replies
5
Views
3,112
I am having trouble with getting no control of my analog output signal. I am using the SCL function block to control my analog output. The logic...
Replies
11
Views
245
hi all, i have a plc i need to get info from for a site im working on: I have a 1764 Micro Logix 1500 LSP Series C (See Attached Image) im...
Replies
2
Views
374
I currently have a weird issue involving Ethernet IP communication between a ABB CI873 (EthernetIP Module) and a 1756-L83ES. The Layout is as...
Replies
8
Views
752
Back
Top Bottom