Compactlogix IP address

Abdul03

Member
Join Date
Jun 2012
Location
England
Posts
77
Dear Friends,

I know this question might sound very simple.

Can anyone out there help me in setting up the IP address of a compactlogix PLC. I know, one of the option is to do it by BOOTP DHCP service. However, this option is not enabled in the processor.

Can you guys tell me what are the other possible ways to change the IP address, if we dont know the IP and the BOOTP DHCP is not enabled. Or alternatively, what are the possible ways to identify the controllers IP address.

Thank you
 
Connect to the controller via the serial port.(RsLinx, use a DF1 driver). This assumes the serial port is configured for DF1(default). If that has been reconfigured as well, then you'll want to evaluate if you can reset it to default or not(IE, do you have the source code to know what this is trying to do).

You can then browse to the controller and change its IP, or go online using RS5000 and do it that way.
 
Hi John,

Thanks for the reply.

Yes I beleive, I can. However, I do not have access to serial cable or any other communication cable at the moment except ethernet and I am trying to find the IP address of the processor.

It's compactlogix L32e.

I am trying to locate the IPaddress of all the devices connected to my computer using a piece of software IPScanner. It shows IP address of all other PC's, but not the PLC.

Is there any other software or method to achieve this ?

Thank you,
 
Wireshark could show you the communications going back and forth. There are other threads on the forum describing how in detail.
 

Similar Topics

I have my PLC and HMI connected to my local network over DHCP just like my laptop. I can upload and download including VNC to the HMI over wifi...
Replies
2
Views
1,138
Hi Guys, I'm trying to get the IP address of my L33ER Compactlogix to show up on my PV+ 600. I know about answer 26779 and have tried it but I...
Replies
17
Views
2,734
I'm trying to configure the IP address of my compactlogix l16er-bb1b in Studio 5000. I need to set it to a certain address as I'm planning on...
Replies
5
Views
3,225
Hi, I have a compactlogix 5069-L330ERM processor, which has 2 built in ethernet ports. Both are currently configured and was completed using...
Replies
20
Views
8,909
We have some vendor supplied machinery that runs on a CompactLogix 5370 (1769-L24ER-EBFC1B, FW rev. 28.011) that wasn't communicating with the...
Replies
6
Views
2,921
Back
Top Bottom