I have several 4-20mA inputs coming from all over the plant into a RA ControlLogix system. Many of these are going into totalizers, being displayed, etc.

What is the best way using RSLogix 5000 (v19) to filter the low mA signals. For example if I have a 0 to 2000 bpd flow meter, a slight 4mA noise will read 1 to 2 bpd. I want to filter that such that it only displays or totalizes when say the flow is over 10 bpd.

What is your best suggestion. I have some logic in place to do this already, but it is crude and I figure the wizards around here might have a great idea.

Thanks!
 
Low flow cut-off.

If flow less then 10 move 0 to register used for totalizer.
If flow is equal to or greater then 10 move actual value to register used for totalizer.
 

Similar Topics

Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
Replies
2
Views
87
When supplying variable frequency drives (vfd), should we install the line filter (emc) before the reactor (choke), or reactor before filter...
Replies
2
Views
196
Hi. I'd like to have a filter on an Alarm Summary page where I could pick which of the 3 groups I created I want to display on the screen. I...
Replies
3
Views
547
Good morning, I'm new to PLC and HMIs, and I was given the following problem: I need to be able to filter alarms and events that are only related...
Replies
0
Views
389
I am trying to find the operating limit range of a few conveyors. In the event one of them breaks I want to see the abnormal value and use this...
Replies
11
Views
1,324
Back
Top Bottom