I have a AB 1769-L24ER plc
I have setup a variable to count run time of a motor, it work fine, but when I do a full download the variable get reset is there a way to make it completly retained?

Thanks
 
If you save your file while online the software will ask if you want to upload the tag values - say 'yes' - then your PC will have the same data as the PLC
 
julspower said:
...is there a way to make it completly retained?

danatomega said:
If you save your file while online the software will ask if you want to upload the tag values - say 'yes' - then your PC will have the same data as the PLC

Only if the motor is stopped when you Upload. If you Upload while the motor is running then the running time will further increment before you stop the motor and perform the Download. The computer will not have the same data as the controller.

I may be splitting hairs if a few seconds or even minutes do not matter, but worth noting I feel?

Regards,
George
 
No, to my knowledge, (please correct if need be) there is no way to make tag data "completely retained" or write protected during a download. In COmpactlogix the tag data is part of the program so it all comes in together.

There is a way to do what you want.
Its called the Rockwell Software "Tag Upload/Download Tool"

http://www.software.rockwell.com/support/download/detail.cfm?ID=3718

You use this to save all your most current tag data to your laptop.
You can then download the program.
The you write the tag data saved above back to your processor.

Everything is as it was.
 
Only if the motor is stopped when you Upload. If you Upload while the motor is running then the running time will further increment before you stop the motor and perform the Download. The computer will not have the same data as the controller.

I may be splitting hairs if a few seconds or even minutes do not matter, but worth noting I feel?

Regards,
George

George, you are completely correct (go ahead and split those hairs - in many circumstances it's important) - I didn't even consider the motor running time and otherwise active data...
 
GTUnit said:
No, to my knowledge, (please correct if need be) there is no way to make tag data "completely retained" or write protected during a download...

GTUnit,

Yes, actually there is, but I'll get to that later.

The Tag Upload/Download Utility is one option if the OP is looking to save one or more tag data values for various reasons including before performing a Download.

However, it had appeared to me that they just wanted to find a "simple" way to make "it completly retained". That is, just the running time tag value.

If you simply Upload that value, while static, make edits that do not affect it, and then Download, it will be retained, even if the controller is power cycled.

Another simple option is to take note of the value, when static, before performing the Download and then write that value back to the tag when done. But that requires a user remembering to do this.

If you have a situation where you want to retain several, many or all tag values, then yes, you would be better to look at other options...

I say "simple" above because the Tag Upload/Download Utility is not so simple an option. You must have an OPC compatible version of RSLinx Classic with an OPC Topic setup to the controller. RSLinx Classic Lite will not suffice. A Single Node licence minimum would be required for a single controller. You must also select, via the Tag Upload Download Tool, which tags you want to exchange via OPC. Once the tag value is saved, and the Download performed, you must once again select the data, using the Tag Upload Download Tool, that you want to restore, and manually update it. This method, while somewhat more involved, does have its advantages. You can select just the tags you require and you can use it while the controller is in Run Mode. This is it's primary advantage really.

The better option, for preserving tag data values, before performing a Download, is to use the Data Preserve Download Tool. This tool can be used, manually or automatically, to save all supported tags and their values to a CSV file. The CSV file is then later used to restore the tag values in the controller.

In Auto, it will Upload tag values and save then to a CSV file. Next it automatically performs an ACD file Download. Then it automatically Downloads the tag values from the CSV file into the controller. While the advantage here is that this is all done automatically for you, and without OPC, there are disadvantages. You can only preserve and restore all supported tags, and not individual tags, and the controller must be placed in Program Mode.

Regards,
George
 

Similar Topics

I have a 1769-L24ER-BB1B and I am trying to flash it to 34xx, its flashing red and faulted, when I try to flash it I get a popup stating it needs...
Replies
14
Views
276
Hello all, and thank you in advance for any assistance you may be able to provide! This is my first post, so if I need to reformat or change...
Replies
8
Views
511
Hi everyone: I went to AB.com, found only firmware, no EDs file showing up. i took a pix of device properties of RSLinx. Thanks
Replies
1
Views
140
hello plc professionals , i have a plc AB 1769-l24er and 13 VFD AB 525 and HMI and STRAIX 2000 unmanaged switch .. the LOGIX Designer limiting me...
Replies
6
Views
1,545
Hi All, I have a small project using a 1769-L24ER-QB1B and I am trying to get a jump on the project by setting up the software before the...
Replies
7
Views
2,251
Back
Top Bottom