I am trying to assist someone with downloading a program to a TSX Premium over the Ethernet module port. Don't have the serial cable. How do you set up the comms for Ethernet, in the PL7 v4.5 SP5 software. Have no experience with this software. Also, do you have to set your laptop network adapter to match the IP series, like many other Ethernet connections? (Example: PLC is 192.168.20.20 so laptop should be 192.168.20.xx) Any assistance greatly appreciated!!

Snag-0170.jpg
 
you need xip driver for this at PL7. computer and plc have to be at same subnet/ address area.

On control panel (if you have installed xip-driver)

open schneider drivers manager.

On xip driver, give some xip address for plc. Bind your network card with driver and make driver active (save + start)
On xip driver you can also ping you plc, it should work.

On PL7 you need connect with this xip address to plc. select PLC -> Define plc address, give xip address with {x.x}sys and select driver xip (default is unitelway)

-> ok -> plc -> connect

of course before this your plc and ethernet card need also configured with serial programming cable.

http://control.com/thread/1026221388#1026221388

pl7.jpg
 

Similar Topics

I have a relatively small network but I am having some issues with PowerFlex 755 drives (using the native ethernet card) Faulting with the F926...
Replies
0
Views
230
I have set up comms between an S7-1512SP-1 PN plc programmed with TIA v17 and an S7-314C programmed with Simatic S7 using GET and PUT blocks in...
Replies
4
Views
581
Studio 5000 & PF 525, Ethernet Comms, Encoder FB, Using Motor RPM as speed reference I'm trying to figure out how to send a speed reference in...
Replies
6
Views
970
One of my customers is interested in extracting some data from a machine running on an SLC503 and they really don't want to change the PLC in any...
Replies
5
Views
1,572
I'd like to be able to detect if the Ethernet Comms falls over between my PLC Ethernet card and any of the 5 PF525 inverters I have connected to...
Replies
7
Views
4,935
Back
Top Bottom